208-120vac parallel. Should the grounded conductor be the same size as the ungrounded conductors?
208-120vac parallel. Should the grounded conductor be the same size as the ungrounded conductors?
The grounded conductor(s) must be sized for the load and not necessarily the same as the ungrounded conductors. But be aware that in no case can the grounded conductor(s) be smaller than indicated in Table 250.66 even if there is no load calculated load on the grounded conductor. See 250.24(C).
Not sure exactly which section it is but I think there is an informational note stating that it may be desirable to increase the grounded conductor size in cases where high harmonic currents are expectedl. This is just an informational note though and not a requirement.
That's it.I think kwired is referencing the informational notes pertaining to 220.61.
I am refering to the "grounded" conductor, not the "grounding" conductor.The grounded conductor(s) must be sized for the load and not necessarily the same as the ungrounded conductors. But be aware that in no case can the grounded conductor(s) be smaller than indicated in Table 250.66 even if there is no load calculated load on the grounded conductor. See 250.24(C).
I am refering to the "grounded" conductor, not the "grounding" conductor.
In most case the neutral- ungrounded conductor is sized the same as the grounded conductor in commercial work
well I fixed it-- had my grounded and ungrounded reversed lolhuh?
well I fixed it-- had my grounded and ungrounded reversed lol
I figured... I've never seen a post from you that wasn't absolutely right... that's what shocked mehmy:
well I fixed it-- had my grounded and ungrounded reversed lol
Yes, I thought that was appropriate to leave alone to make sense of realoman's postYou fixed your post, we can still see in the quote what you originally had:happyyes:
For sure-- there are many :lol::lol:I've got some of his I saved... want to see them ??(not really)