Gas Plants Grounding of Equipment to Skids
adam garcia
Spring, texas
Gas Plant Application:
When grounding the BASES of Vessels or Pumps to the SKIDS they are installed on, do you need a PVC protective sleeve over the ground?
I know it is common practice to use PVC Sleeves when going from such equipment to underground ground loop, but am not sure about grounds that stay above ground on top(floor) of Gas Skids.
Not finding in NFPA70 NEC 2011 Handbook, please help.
See if this helps
250.64
(B) Securing and Protection Against Physical Damage. Where exposed, a grounding electrode conductor or its enclosure shall be securely fastened to the surface on which it is carried. Grounding electrode conductors shall be permitted to be installed on or through framing members. A 4 AWG or larger copper or aluminum grounding electrode conductor shall be protected if exposed to physical damage. A 6 AWG grounding electrode conductor that is free from exposure to physical damage shall be permitted to be run along the surface of the building construction without metal covering or protection if it is securely fastened to the construction: otherwise, it shall be protected in rigid metal conduit (RMC), intermediate metal conduit (IMC), rigid polyvinyl chloride conduit (PVC), reinforced thermosetting resin conduit (RTRC), electrical metallic tubing (EMT), or cable armor. Grounding electrode conductors smaller than 6 AWG shall be protected in RMC, IMC, PVC, RTRC, EMT, or cable armor
Yes, thanks this answers my question because my wire is #2 AWG. Thanks
See if this helps
250.64
See if this helps
250.64
is this a GEC or is it an EGC? I am thinking the latter rather than the former.
See if this helps
250.64
250.120 Equipment Grounding Conductor Installation.
(C) Equipment Grounding Conductors Smaller Than 6 AWG. Where not routed with circuit conductors as permitted in 250.130(C) and 250.134(B) Exception No. 2, equipment grounding conductors smaller than 6 AWG shall be protected from physical damage by an identified raceway or cable armor unless installed within hollow spaces of the framing members of buildings or structures and where not subject to physical damage.