Is SE Cable Plenum Rated?

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
True. My error.
I find nothing on Soutwire's site as to it being plenum rated.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
Seems like it would be on their spec sheet if it was (even as an option), huh.

Under the specification there is no listing for ASTME 84 testing protocol for materials suitable for installation in plenums 25 Flame spread/50 Smoke development.

I would say no
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Is there anywhere in the code that states nm is plenum rated? If it were plenum rated it would be on the cable. I have never seen se cable with plenum rating but I don't use it often.
 