Aluminum wire for AC runs?

Status
Not open for further replies.

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
The difference in cost between Cu and Al wiring for a long AC run in a large system can be many thousands of dollars, and margins are thin. What say you?
 

mayanees

Senior Member
Location
Westminster, MD
Occupation
Electrical Engineer and Master Electrician
We did a 480 Volt, 3000-amp aluminum run for a well-known online seller's Data Center, at a very significant savings. As long as the terminations are done right, and are accessible for thermal and physical inspections, it makes good sense. They went from the outdoor padmount transformer in to the switchgear.
John M
 
Last edited: