GfCi
Jerseydaze
In New Jersey do we need to put GFCIs on sump pumps in unfinished basements or did that part of the code get thrown out?
Below is the appropriate modifications to the NEC 210.8 that applies to New Jersey from the Uniform Construction Code. If this is a dedicated outlet for the sump pump then GFCI protection would not be required.
? 5:23-3.16 Electrical subcode​
3. Chapter 2 of the electrical subcode, entitled "Wiring and Protection," is amended as follows:i. Section 210.8(A)(2) and (5) of Article 210, entitled Branch Circuits, is deleted; it is replaced by Section 210.8(A)(2) and (5) and the exceptions in the National Electrical Code 2005 as follows:
"210.8(A)(2) - Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas ofsimilar use.
Exception No. 1 to (2) - Receptacles that are not readily accessible.
Exception No. 2 to (2) - A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)7, or (A)(8).
Receptacles installed under the exceptions to 210.8(A)(2) shall not be considered as meeting the requirements of 210.52(G).210.8(A)(5) - Unfinished basements: For purposes of this section, unfinished basements are defined as portions or areas of the basement not intended as habitable rooms and limited to storage areas, work areas, and the like.
Exception No. 1 to (5) - Receptacles that are not readily accessible.
Exception No. 2 to (5) - A single receptacle or a duplex receptacle for two appliances locatedwithin dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)7, or (A)(8).
Exception No. 3 to (5) - A receptacle supplying only a permanently installed fire alarm or burglar
alarm system shall not be required to have ground-fault circuit-interrupter protection.