Natfuelbilll
Senior Member
Howdy Folks -
An existing primary fed 4.16kV service supplying multiple buildings in a campus setting.
One new load (a large motor) is being installed at a unique location not next to, or near, any if the existing buildings.
Two choices
1. Extend the primary and buy a new switch and xfmr. $$$ due to 100's of feet separation.
2. Install a new service into the PROPERTY straight from the utility. $ Due to relative short distance from utility to new 480v motor load.
Is this a 230.2 issue?
"Different Characteristics. Additional services shall be permitted for different voltages"
I favor the 2. to save $$
What say you?