Thanks for the references. I will put my study hat on
Hazardous locations isn’t rocket science but it is a bit more than common sense. If it were only common sense, we probably wouldn’t worry about Divisions or Zones. In Class I, we would just build to Division 1 and not look back.
Think in terms of the fire triangle (fuel, oxidizing agent, ignition source) where oxygen (the most common oxidizing agent) will constantly be available.
In Division 1, fuel is also available often enough in “normal” operations so we attempt to protect against both common and uncommon sources of ignition. Division 1 is actually easy to design for; there are few options available. But it’s generally too expensive for overall use.
In Division 2, fuel is not commonly available so typically we only try to avoid common sources of ignition; i.e., arcs, sparks and high temperatures (ASH) that occur while the installation is behaving normally. It takes more knowledge and judgment to apply.
If you review the protection techniques in Section 500.7 and their scopes of protection you will see they generally attempt to deal with fuel or ignition sources or both. Note that
explosionproof
only deals with Class I. See the definition in Section 500.2
In Division 2, explosionproof equipment is not always required. But, unless some other protection technique is properly applied, it is required for any ASH components. In some cases, explosionproof equipment may be used, but not required.
Where explosionproof equipment
is required in Division 2, seals are required to maintain the integrity of the enclosure. Also any wiring method between the enclosure and the seal must also be suitable to maintain the explosionproof integrity and only Division 1 wiring methods are suitable for that.
BTW for those that feel compelled to bring up Zones as an alternative, we wouldn’t even worry about them if “…we would just build to Division 1 and not look back.” Ultimately, the analysis would remain the same for
flameproof unless you wanted to somehow only build for Zone 0.