Elexit
 - Austin, Texas
It is clear that 690.14 requires a PV system to have no more than six disconnects, and that they are required to be grouped together, just as service disconnects are limited by 230.71. But at what point are we counting? Until recently, we could say that if all inverter outputs are combined in a panelboard, and that panelboard has a main breaker or main switch, we have satisfied this rule, as this AC switch serves to "disconnect all current-carrying conductors of a photovoltaic system from all other conductors in a building or structure."
Then the 2011 NEC specified that this provision applies to the DC disconnecting means. Now we have a problem if we want to install a system with more than six inverters. Or do we?
Look at the definition in 690.2:
If I have eight string inverters, each with its own array, combiner box, and disconnects; and if I open seven of the eight breakers in my aggregation panelboard, the one remaining inverter and array functions as designed. It is a complete system, which could be installed by itself and pass inspection. If this meets the NEC definition of a PV system, as I believe it does, then what we have is a group of eight systems, each of which is allowed to have up to six disconnects.
The problem is that the NEC definition is not as specific as the MPP bus of an inverter. If I have eight buildings on a campus fed from a single medium voltage service, and each building has a PV system with an interconnection in that building, then no one would argue that I don?t have eight systems instead of one. But put all of the arrays and inverters on one building, and the aggregate thereof ?wants? to be called a system.
Presently we are designing a system for two carport structures atop a parking garage. We want to use eight PowerOne Aurora TRIO inverters, and the customer would like them placed in a room at grade level. Our AHJ has been equivocal about what we can do to satisfy the Code requirements, but three inspectors in the department agree that the six-handle rule appears to apply here. Yet I find it hard to believe that the intent of the Code is to restrict design to six or fewer inverters.
If we could install a group of four disconnects on each carport, that would address the intent of this section: to limit the number of operations of the hand, and the amount of time a firefighter spends walking around looking for them. It would not, however, strictly comply with a rule derived from a 1937 precedent designed to apply to energy from a single source (utility transformer).
I've read the 2014 CMP 4 proposals, and I still don't fully understand the requirement. Any ideas?
Solar Photovoltaic System. The total components and subsystems that, in combination, convert solar energy into electric energy suitable for connection to a utilization load.