- Location
- Windsor, CO NEC: 2017
- Occupation
- Hospital Master Electrician
I'm trying to accurately recreate a Neutral-Earth-Voltage scenario, using Ohm's Law to demonstrate.
I have a problem. I can't realistically expect to find 62V between an EGC and remote earth, right? I thought NEV was usually 2v to 8v.
I'm trying to accurately recreate a Neutral-Earth-Voltage scenario, using Ohm's Law to demonstrate.
I have a problem. I can't realistically expect to find 62V between an EGC and remote earth, right? I thought NEV was usually 2v to 8v.
View attachment 8322
So you have zero Ohms from the pool bonding to the XF neutral?
I may be missing something here. The 346 volts is coming from where? Shouldn't it be a heat loss in the line? I2R
I'm thinking it's one or several of several potential errors:
1. 20A over 10 miles is unrealistic, creating an insane amount of voltage drop.
2. The MGN resistance contributions (neighboring houses) between the substation and our house are underestimated.
3. I've got some basic concept missing that would fix the difference.
Edit to add:
4. 13.8 kV not being common for this application?
1) The 20 amps would be spread out over 10 miles and is low. Realistically it could be upwards of 100 amps. That is still only 1400 kW. Also there would probably be a regulator somewhere on the line.
2)The Zero at the house is probably too low, so are the ground resistances. I realize 25 ohms is recommended, but 25 ohms today may be 90 ohms next week.
The 346 volts isn't returning. It is a power loss (I2R)
I am trying to demonstrate the voltage between a swimming pool and remote earth under normal operating conditions.
I threw in neighboring houses' electrodes that would be physically connected via the primary neutral, which is the 1Ω towards the left, in the field of power poles. It helped, but didn't bring the numbers down to reality. :happyno:
Not sure if it will help or not, but you cannot assume that the voltage drop across the 10 mile line is acting equally at all of the intermediate grounds that are contributing to your estimated 1 ohm to ground.Possibly your primary current, and therefore wired neutral voltage drop, is too high? Or the primary resistance value is too high. Will take another look.
I was suggesting real life amperages, regardless what it does to the numbers.Increasing the amperage would drive the theoretical NEV up, not down.
I was referring to the Ohm values used on the poles for the 25 ohms, and around here ufers aren't really used much. The two rods are used, and the values could be 25 one wet day, and 90 ohms in the summer.I'd beg to differ on that. A Ufer should hang in at around 5Ω resistance to earth, and a pool should be close to the same value.
You are certainly welcome. I did run another scenario similar to your graphic and get around 18-20 volts for an end-of-the-feeder scenario of 20 amps of unbalanced feeder current. While this is probably a fringe case, it is important to remember what we are doing at the pool. We are trying to create an equipotential area.I'm not worthy!
Thanks Mivey.![]()
Should have read:Earth voltage about 50 feet away from everything is about 60-80 volts. Earth voltage about 50 feet away from everything is about 30-50 volts.