adalewhite
Master Electrician, Electrical Design, Veteran
- Location
- Georgia
- Occupation
- Licensed Electrician, Electrical Designer, A&E PM
There are 3 sets of 4? conduits each with 4-600kCMIL conductors are required by the contract documents. Only two sets are installed at first and it is caught on a punch list and the third set is required to be installed. The follow up punch list reads ?While the third 4? conduit has been added to the service entrance, the pull box violates NEC 314.28. The box dimensions should be at least 4?X6=24?+4?+4?+32? in width and 8? deep per 314.28(A)(2) Exception reference to Table 312.6(A) for entry in the wall of box opposite a removable cover.? Is this a correct call? See the pictures.


