30 Amp receptacle circuit ?
ToolHound
I'm looking at 210.23 (Permissable loads) and
T210.24 (Summary of Branch Circuit Requirements),
both copied below.
Crazy question: is it conceivable to have 120 volt receptacles on a 30A branch circuit ?
Never seen it, but 210.23 may permit it?
Are there 120 volt receptacles on the market rated 30A ?
Table 210.24 Summary of Branch-Circuit Requirements
Circuit Rating​
15 A​
20 A​
30 A​
40 A​
50 A​
Conductors (min. size):​
Circuit wires1​
14​
12​
10​
8​
6​
Taps​
14​
14​
14​
12​
12​
Fixture wires and cords
? see 240.5​
Overcurrent Protection
15 A
20 A
30 A
40 A
50 A
Outlet devices:​
Lampholders permitted​
Any type​
Any type​
Heavy duty​
Heavy duty​
Heavy duty​
Receptacle rating2​
15 max. A​
15 or 20 A​
30 A​
40 or 50 A​
50 A​
Maximum Load
15 A
20 A
30 A
40 A
50 A
Permissible load​
See 210.23(A)​
See 210.23(A)​
See 210.23(B)​
See 210.23(C)​
See 210.23(C)​
1These gauges are for copper conductors.
2For receptacle rating of cord-connected electric-discharge luminaires, see 410.62(C).
Code and Commentary, from NEC NFPA-70 Handbook, quote:
210.23 Permissible Loads.
In no case shall the load exceed the branch-circuit ampere rating. An individual branch circuit shall be permitted to supply any load for which it is rated. A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size as specified in 210.23(A) through (D) and as summarized in 210.24 and Table 210.24.
According to 210.23, an individual (single-outlet) branch circuit can supply any load within its rating.
(A)
15- and 20-Ampere Branch Circuits. A 15- or 20-ampere branch circuit shall be permitted to supply lighting units or other utilization equipment, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2).
Exception: The small-appliance branch circuits, laundry branch circuits, and bathroom branch circuits required in a dwelling unit(s) by 210.11(C)(1), (C)(2), and (C)(3) shall supply only the receptacle outlets specified in that section.
(1) Cord-and-Plug-Connected Equipment Not Fastened in Place. The rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.
(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires, shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.
Section 210.23(A)(2) permits a 15- or 20-ampere branch circuit supplying lighting outlets to also supply utilization equipment fastened in place, such as appliances or an air conditioner. Under the conditions specified in this requirement, the utilization equipment load must not exceed 50 percent of the branch-circuit ampere rating (7.5 amperes on a 15-ampere circuit and 10 amperes on a 20-ampere circuit). However, according to 210.52(B), such fastened-in-place equipment is not permitted on the small-appliance branch circuits required in a kitchen, dining room, and so on. The requirement in 210.23(A)(1) clarifies that only cord-and-plug-connected utilization equipment that is not fastened in place can have a rating of up to 80 percent of the branch-circuit rating where the circuit also supplies other loads. Equipment that is fastened in place, whether direct wired or cord and plug connected (waste disposers and dishwashers, for example), is covered by the 50-percent requirement in 210.23(A)(2). The requirements of 210.23(A)(2) do not apply to a branch circuit that supplies only fastened-in-place utilization equipment, and where that is the case the entire rating of the branch circuit can be applied to the utilization equipment. For example, a 20-ampere branch circuit dedicated to supplying a waste disposer and a dishwasher is not restricted to either one of the appliances not exceeding 50 percent (10 amperes) of the branch-circuit rating as long as the combined load of the two appliances does not exceed 20 amperes.
(B) 30-Ampere Branch Circuits. A 30-ampere branch circuit shall be permitted to supply fixed lighting units with heavy-duty lampholders in other than a dwelling unit(s) or utilization equipment in any occupancy. A rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating.
(C) 40- and 50-Ampere Branch Circuits. A 40- or 50-ampere branch circuit shall be permitted to supply cooking appliances that are fastened in place in any occupancy. In other than dwelling units, such circuits shall be permitted to supply fixed lighting units with heavy-duty lampholders, infrared heating units, or other utilization equipment.
(D) Branch Circuits Larger Than 50 Amperes. Branch circuits larger than 50 amperes shall supply only nonlighting outlet loads.
See the commentary following 210.3, Exception, regarding multioutlet branch circuits greater than 50 amperes that are permitted to supply nonlighting outlet loads at industrial premises.
--Thanks.
As pointed out, there are 30 A 125V receptacles. They are typically only used for limited equipment that would require additional ampacity than a 15 or 20 amp circuit would provide. There is no interchanging between 15 and 20 amp receptacles as the configuration of the plug is completely different, so items with 15 and 20 amp cord caps will not plug into a 30 amp receptacle, unlike how a 15 amp cord cap will plug into a 20 amp receptacle.
To add to that there are 30A 125V plugs/receptacles for travel trailers also. Those who do construction /service in food service can confirm if 30A 120V circuits are still used for some commercial coffee makers.