- Chapel Hill, NC
- Retired Electrical Contractor
I was at the state meeting in Raleigh this week and Jeff Fecteau from UL was on the board answering questions. He stated that the standard red and yellow wirenuts weren't listed for Class C wire. If you go to Chapter 9 Table 10 you will see that #12 wire has 7 strands and is rated Class B. However rubber cord such as SJO and the like is rated Class C with 19 strands. This means that you cannot connect the wires in sjo cord with the standard wirenuts. I included the link to UL-- do you all read it the same way?
Here is what I found in UL book
Stranded conductor Class — Connectors rated for use with stranded conductors are for the following strand configurations:
Aluminum – Class B concentric, compressed or compact, and SIW (.single input wire)
Copper-clad aluminum – Class B concentric or compressed, and Class C concentric
Copper – Class B concentric or compressed, and Class C concentric Wire connectors additionally rated for use with compact copper conductors are additionally marked ‘‘For compact-stranded copper conductors’’ or equivalent on the connector, or on or within the unit container.