I would pick the smallest cable that is protected by the generator output breaker. If you don't know the breaker size, use the generator kVA rating. The kVA rating is usually 125% of the kW rating, but you need to check to be sure. Some small single-phase gensets have kW=kVA.

For 3-phase, I=1000xkVA/(Vx1.732)
For 1-phase, I=1000xkVA/V
 