Bonding cold and hot at the water heater
Mesh
US
I know this subject has some controversy. But I know that the local inspectors want it done so it's easier to just comply. My only question is what size jumper is required?
For a typical 200A service I think a #6 should suffice, but I wonder if a #4 is required like the water pipe GEC.
Which is it?
I think technically it needs to be sized per 250.66 just like the main water bond. However, I put a #6 between hot, cold, and the copper drains and the inspector liked that (I had a 1/0 to the main water pipe because it was a 400A service). The pipe clamps that could take a 1/0 were rather hard to find and I didn't want to buy 3 more, especially one for a 2" copper pipe.
I wish the code allowed interior water pipes to use 250.122 like every other type of pipe type that could be energized.
SO I'll just use some #2 Al and purchase another pair of those expensive dual rated pipe clamps :D
Bonding jumpers are sized per table 250.66, according to the largest ungrounded conductor. You would also use this table when grounding for a 200 amp service and sizing GEC for water meter, water heater, water softener, and ufer ground. The #6 solid bare is the max size you need to use for a 200 amp service ground rod electrode.
Also a CEE (Ufer) GEC or bonding jumper is not required to be larger than #4 even if the corresponding conductor size in T250.66 is larger than #4.
Actually a #6 copper conductor (it doesn't have to be bare) is the maximum size required to a rod type electrode for any size service.
BTW welcome to the forum.
Roger