- NE Nebraska
- EC
What are they not telling you that you need to know?They ought to just tell it like it is on the nameplate.
I don't care what setting the overload device actually trips at, it is part of the listed unit intended to protect its associated motor, it inherently protects the conductor that they also told on the nameplate what the minimum ampacity is to be.
Same goes for a motor with internal overload protection. I don't need to know what the overload actual trip point is to determine what size conductor to run to the motor.
I don't need to know overload trip point when selecting conductors for any other art 430 installation either. If I know I am going to have a 7.5 hp motor I select conductors and overcurrent accordingly to tables. I may not know actual nameplate FLA until a later time, then I will select overload protection device, but conductor was already selected before based on the worst case 7.5 hp motor that may be connected to the circuit via the values in the tables.