ggunn
 - Austin, TX, USA
 - Consulting Electrical Engineer - Photovoltaic Systems
This is correct. This system would have 4 70A backfed breakers on the main, two on each busbar. 140A is 20% of 700A, so 700A is the minimum size of the main. I don't recall if the main is that large.If feeding the grid is a possibility, then 705.12(D)(2), the so-called 120% rule, applies and the Heavy Loaded Panel is undersized. The maximum AC out to the grid is not clear from the manual I have, but can be 56A per SI and there are two on each phase (the SI is 120V), a 70A CB would be used for each SI. Smart $ seems correct.
Just a thought here... Is there any reason why two of the SI's couldn't be left off the main, but only connected to the battery bank and the protected loads panel?