Ohms law
Senior Member
- Location
- Sioux Falls,SD
Can you use bonding locknuts on reducing washers?
Metal reducing washers are considered suitable for grounding for use in circuits over and under 250 V and where installed in accordance with
ANSI/NFPA 70, ‘‘National Electrical Code.’’ Reducing washers are intended for use with metal enclosures having a minimum thickness of 0.053 in. for non-service conductors only. Reducing washers may be installed in enclosures provided with concentric or eccentric knockouts, only after all of the concentric and eccentric rings have been removed. However, those enclosures containing concentric and eccentric knockouts that have been Listed for bonding purposes may be used with reducing washers without all knockouts being removed
You can but it is not neccessary. A better way to do this (from meter socket to another enclosure) is with PVC, that way you have done away with the parallel neutral path.Can I use a bonding locknut on a service ran in EMT from the meter socket to panel? Bonding locknut is in meter socket side.
I am confused now.. It seems we are saying that a service metal raceway does not need special bonding to panels via grounding locknuts or grounding bushings. Is this correct?
If you install the reducing washers correctly for bonding than a bonding locknut is not required.
Chris
You can but it is not neccessary. A better way to do this (from meter socket to another enclosure) is with PVC, that way you have done away with the parallel neutral path.
Roger
As I read it, metallic service conduits must be bonded by one of the methods shown in 250.92.
I've always felt reducing washers would impair such a connection, but, apparently, if installed per listing, with the use of a grounding locknut, they are acceptable.
Okay that was my take but Roger's statement that a bonding locknut was not needed seemed to imply that no other bonding other than a standard locknut was required.
Period? or can be used with bonding bushings? I agree a bonding locknut would not be compliant with reducers.Per the UL White Book,
Reducing washers can't be used for bonding on the line side of the service.
Chris
Explain what you mean correctly. Isn't this a no brainer?
Period? or can be used with bonding bushings? I agree a bonding locknut would not be compliant with reducers.
If you use bonding bushings the reducing washers are not used for bonding just for a mechanical connection.
Chris
You can but it is not neccessary. A better way to do this (from meter socket to another enclosure) is with PVC, that way you have done away with the parallel neutral path.
Roger
I am confused now.. It seems we are saying that a service metal raceway does not need special bonding to panels via grounding locknuts or grounding bushings. Is this correct?
Dennis, Chris is correct, I was meaning PVC would negate the need to bond the metallic raceway. I agree that 250.92(B) requires special attention to bonding of metal raceways at service equipment.Roger's statement was to use PVC conduit between the meter and the service disconnecting means and by doing that bonding locknuts are not needed as the PVC does not require bonding.
Chris