There is nothing in 310.15(B)(7) that allows parallel conductors. IMO, you must use Table 310.15(B)(16)
Couldnt the parallel conducter tables also apply considering your getting an equivalent though to the dwelling table?
Note 3 to the ampacity tables in the 1993 code was the equivalent of 310.15(B)(7) in the 2011 code.6-74- (Article 310, Notes to Ampacity Tables of 0 to 2000 Volts, Note 3): Reject
SUBMITTER: R.W. Worthing, Auberry, CA
RECOMMENDATION: Add new text at the beginning of the second sentence to read:
Application of this Note shall not be permitted for conductors connected in parallel.
SUBSTANTIATION: At a recent Section meeting of the 1AEI, the question of the applicability of Note 3 to parallel conductors was
raised. No consensus was established. Actions, by CMP 6, whether in acceptance or rejection of this Proposal, will establish, for the
record,the position of the Panel.
PANEL ACTION: Reject.
PANEL STATEMENT: Conductors 1/0 and larger are permitted to be paralleled by Section 310-4. This would apply to Note 3.
NUMBER OF PANEL MEMBERS ELIGIBLETO VOTE: 10
VOTE ON PANEL ACTION:
AFFIRMATIVE: 10
That leaves a big question on how to determine the proper size parallel conductors. For example, 1/0 is okay for a 175 service, 350kcmil okay for a 350A service. So is parallel 1/0 okay for a 350A service? If we look at Table 310.15(B)(16) 1/0 is rated 150A, 350kcmil is rated 310A... thus two 1/0 would not equal or exceed the rating of a single 350kcmil.CMP 6 does not agree. The following is a proposal and panel action for the 1996 code
The CMP did not give any guidance with their answer. I would say that parallel 1/0s would be good for a 350 amp service based on their comment.That leaves a big question on how to determine the proper size parallel conductors. For example, 1/0 is okay for a 175 service, 350kcmil okay for a 350A service. So is parallel 1/0 okay for a 350A service? If we look at Table 310.15(B)(16) 1/0 is rated 150A, 350kcmil is rated 310A... thus two 1/0 would not equal or exceed the rating of a single 350kcmil.
"3W" defines the system, not the number of conductors used in the system.But, I thought that the basis for that table is historical data from POCOs for 3W 240 1P services.:?
Agreed. More specifically, the word "ampacity" does not appear anywhere in that table. The table is a "permission granted" opportunity, not a "here is another way to look at ampacity" opportunity.There is nothing in 310.15(B)(7) that allows parallel conductors. IMO, you must use Table 310.15(B)(16)
I think someone mentioned in another thread, there is an accepted proposal to change the section in the 2014 NEC edition... anyone know what that entails?Agreed. More specifically, the word "ampacity" does not appear anywhere in that table. The table is a "permission granted" opportunity, not a "here is another way to look at ampacity" opportunity.
I once submitted a proposal similar to the one Don quotes above. Mine was rejected for essentially the same reason, and with essentially the same lack of clarification. What I would like the CMP to do is to change the title or instructions of the table to explicitly state that the numbers represent allowable ampacities, so that we can clearly parallel conductors in order to get higher ampacities. Right now, all it says is that for this specific installation you can use this specific wire.
It is a calculation now and the table is gone. The main power rule for feeders is gone also.
(7) 120/240 Volt, Single-Phase Dwelling Services and
Feeders.
For service and feeder conductors of 120/240-
volt, single-phase, individual dwelling unit one-family,
two-family, and multifamily service ratings from 100 am-
peres through 400 amperes, an adjustment factor of 0.83 of
the service ampere rating shall be permitted to be used to
determine the size of the ungrounded conductors. The
grounded conductor shall be permitted to be smaller than
the ungrounded conductors, provided that the requirements
of 215.2, 220.61, and 230.42 are met.
[ROP 6?49a]
Yes, but note the word I emphasized. It will only affect feeders requiring an ampacity greater than 83% of the service rating.
I probably need some caffeine too. It's not really a big issue. Let's take a 200A service as an example.I probably just need more coffee, but I do not understand.
200A ? 0.83 =166A
No feeder supplied by this service will be required to have an ampacity greater than 166A.