Fulthrotl
~Autocorrect is My Worst Enema.~
 - E
looks like i'm gonna be needing one in the next week....
any suggestions on brands, and from what i gathered from
my training on the subject, suits above 40 calorie weren't
much benefit, as the blast would most likely be lethal.
dunno if that is true, so i'm asking here. if there is merit
in having a suit above 40 cal, i'd like to know.
im gonna be recommissioning some switchgear that has
been off for a good long while.... and while i can megger
all the feeders, and be comfortable that they aren't
gonna fault, the molded case breakers are another question
entirely. while i can megger them phase to phase, and phase
to ground, there is a question in my mind as to their capability
to contain a fault... they are circa 1965, and have been turned off
right near the water, exposed in a tin building, with an open
door so all the weather is right there. it's all been dead and
dark, going on a decade. not getting rained on, but nice cold
wet fog.
the 1,200 amp 480 delta breaker feeding all this
from 300 yards away is a 65k interrupting rating,
and that piece of 3R gear is pretty new, and confidence
inspiring. call it less than 10 years old.
the old stuff is not reassuring, to the extent that i'm gonna
megger and document everything, and if it looks all good,
close and lock the questionable gear, and energize it from
the 1,200 amp gear, 300 yards away.
i still want a suit, period.
suggestions, anyone? some of the smartest gear and
breaker folks i know are on here.... what say you?
wet fog.