These two sections have been in the Code since 1975 or earlier in someway, shape, different number or slightly different text.
I've looked in NEC handbooks back 1996. No help. I've read 408.36 EX 2 over the years and have never known what it applied to.
What does two main circuit breakers having a combined ratingnot more than that of the panelboard mean? Two supplies to the panel? So wecould have two 100amp feeders supplying a 225 amp bus panelboard? Doesn?t seemright.
If I have a 200 amp C/B in the service and a 200 amp C/B aspanelboard main, I wouldn?t combine the rating of the two and say the panelboard is protectedby 400 amps.
And if I can have two 100 amp supplies to a 225 amppanelboard, how does 240.8 fit in where it says breakers cannot be connected inparallel?
This post relates to the thread going in PV forum
http://forums.mikeholt.com/showthread.php?t=152928
I've looked in NEC handbooks back 1996. No help. I've read 408.36 EX 2 over the years and have never known what it applied to.
What does two main circuit breakers having a combined ratingnot more than that of the panelboard mean? Two supplies to the panel? So wecould have two 100amp feeders supplying a 225 amp bus panelboard? Doesn?t seemright.
If I have a 200 amp C/B in the service and a 200 amp C/B aspanelboard main, I wouldn?t combine the rating of the two and say the panelboard is protectedby 400 amps.
And if I can have two 100 amp supplies to a 225 amppanelboard, how does 240.8 fit in where it says breakers cannot be connected inparallel?
This post relates to the thread going in PV forum
http://forums.mikeholt.com/showthread.php?t=152928