I am working with a panel builder and I need to find the code or standard that has an issue with bundling 120VAC power for motors (1hp @ 16 A) with 24Vdc control wires. Personnally, it is a bad idea but I have to come up with a code or a standard violation for him to make 2 runs.
Burchie
690.4 Installation.
(A) Photovoltaic Systems. Photovoltaic systems shall be permitted to supply a building or other structure in addition to any other electricity supply system(s).
(B) Identification and Grouping. Photovoltaic source circuits and PV output circuits shall not be contained in the same raceway, cable tray, cable, outlet box, junction box, or similar fitting as conductors, feeders, or branch circuits of other non-PV systems, unless the conductors of the different systems are separated by a partition. Photovoltaic system conductors shall be identified and grouped as required by 690.4(B)(1) through (4). The means of identification shall be permitted by separate color coding, marking tape, tagging, or other approved means.