prhart
New member
- Location
- Willits,CA Mendocino
in an outlet box with one romex 3 wire in and one romex 3 wire out can you use the outlet terminals to pass thru that outlet box or do you have to wire nut them so the pass thru is not the receptacle?
Since you have NM cable you would need to pigtail the EGC's.
Since there is only one grounding screw on the device I was thinking that was self explanatory but you never no how determined someone might be.![]()
Yes, there is a prohibition for this. The EGC path can't depend on the device (similar to a neutral in a MWBC). Sorry, but I don't have my code book readily available so I can't site the exact 250.XX.I threw it out there because I'm unsure if pigtailing the EGC is specifically required by the NEC. Is there a prohibition for making a device which will accept more than one EGC?
I threw it out there because I'm unsure if pigtailing the EGC is specifically required by the NEC. Is there a prohibition for making a device which will accept more than one EGC?
250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes.
(B) Grounding Continuity. The arrangement of grounding connections shall be such that the disconnection or the removal of a receptacle, luminaire, or other device fed from the box does not interfere with or interrupt the grounding continuity
250.148(B) Grounding Continuity. The arrangement of grounding
connections shall be such that the disconnection or the
removal of a receptacle, luminaire, or other device fed from
the box does not interfere with or interrupt the grounding
continuity.
If you think about it even devices with pressure plate terminations are designed to accept only one EGC.
If you think about it even devices with pressure plate terminations are designed to accept only one EGC.