GUNNING
- Gainesville, Florida
Ive got a customer that wants his doublewide 3000 sq ft MH with gas appliances changed to all electric. The existing Water heater is electric but the heating, range and stove are gas. They want to remove the existing gas stove top and oven and install a new electric oven, electric stove top, and microwave plus an electric heatpump package unit outside removing the existing inside gas furnace and condenser. I figure it will be an additional 22.5 kw at 35% or 32 amps increase on the service overall. It was built in 86 and has a 100 amp panel inside off of a 150 amp service.
I can't find the boiler plate with the service size for the home because they covered it up with a mud room. I am pretty sure the MH mfg figured on maximizing the size of the inside panel. Can I run the new appliances off the outside service panel? Should I increase the size of the panel inside and run them from inside? Should I run the new appliances off of the existing 100 amp panel? They would be removing 2 1500 watt small appliance circuits or 3000 watts. They want to replace it with a stove, microwave, and oven, or 13Kw. Is this possible given the boilerplate and that I am not a MH mfg? It would only be 35% of the 13Kw or 19 amp calculated additional load on the inside panel.
Q: can I run the new appliances inside from the outside panel ?
Q: can I increase the size of the inside service (and feeder) and run the new appliances from that, even though the boiler plate is obscured, but we know it is 100 amp?
Q: can I do a new load calculation on the MH and use that to justify the service size and still be legal?