Transformer sizing

Status
Not open for further replies.

Timboe

Member
We just got a new machine at work. The problem is it is set up for 3 phase 208v. The machine is rated at 14.5 amps at 208v I will need to purchase a transformer from 480v 3phase to 208 to run the machine. Would I need to purchase a 1.5kva or do I need a different kva transformer?
Thanks timboe
 

Timboe

Member
Wait I think my 1.5kva is all wrong. What size kva do I need because it needs to be all 3phase 480v primary 208v secondary for 14.5amps at 208v
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
My math comes up as 5.2 kva. 6 kva would be the next standard 3 phase transformer.
If it's primarily a motor load you might run the stats by your suppliers they might recommend a 9 kva depending on starting data.
(Torque, number of starts, etc.)
 