We sent a guy to a service call where the home owner had some receptacles not working. He found a bad connection in one of the boxes and got the circuit working again with the exception that he is only getting 90v to ground. I was wondering if 406.4 (D)(2)(b) would apply until the circuit could be more thoroughly diagnosed even though the existing devices are 3-wire? Does it only apply to two-wire circuits and devices? What is an acceptable line voltage-to-ground?
(D) Replacements.
(2) Non?Grounding-Type Receptacles. Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(2)(a), (D)(2)(b), or (D)(2)(c). See related UL
(a) A non?grounding-type receptacle(s) shall be permitted to be replaced with another non?grounding-type receptacle(s).
(b) A non?grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked ?No Equipment Ground.? An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.
(c) A non?grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked ?GFCI Protected? and ?No Equipment Ground.? An equipment grounding conductor shall not be connected between the grounding-type receptacles.
(D) Replacements.
(2) Non?Grounding-Type Receptacles. Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(2)(a), (D)(2)(b), or (D)(2)(c). See related UL
(a) A non?grounding-type receptacle(s) shall be permitted to be replaced with another non?grounding-type receptacle(s).
(b) A non?grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked ?No Equipment Ground.? An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.
(c) A non?grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked ?GFCI Protected? and ?No Equipment Ground.? An equipment grounding conductor shall not be connected between the grounding-type receptacles.