mstrlucky74
- NJ
If you change lamps to a higher wattage does that change the load on the circuit or any other previous calculation? Thanks
Unless the original load calculation was based on square footage or fixture rating rather than the actual installed fixtures and lamps.Yes you will change the load on the circuit
The calculations are required to be made using the largest lamps a fixture can use.
+1need more input from the OP all that is known is that you add load when you raise the wattage
He also asked about calculations and those should be all set if done correctly from the start.
+1
What we do not know is whether the OP was interested in actual load or calculated load.