paul
- Snohomish, WA
Situation is we are temp feeding some service gear with a temp generator skid. 480/277. Grounded conductors in the system stop at this gear, first disconnect. We are feeding with DLO 4/0 cables. 8 per phase. 2 for grounding conductors.
Originally I was told no grounded conductor, but when I got there I realized it was the first disconnect and I need to bring my neut and land it. I am planning on bringing only 1 (4/0) to bond.
My question is do I need to match my 2 grounding conductors and bring 2 neutrals over or can I get away with 1? Inspection later this afternoon. Mind you this will all be taken apart and put back together in the original configuration around 3am tomorrow morning.
Thanks.
Edit to add, there is NO load on the grounded conductor.
Thanks.