I agree it is correct however the final ampacity after derating cannot be larger then the 75C column
No.Don't you mean that the final conductor ampacity after derating must greater than or equal to the 75? C rating?
No.
The final conductor ampaciity is the lesser of the derated value or the 75?C column's value.
I agree it is correct however the final ampacity after derating cannot be larger then the 75C column
I know it's not exactly what Dennis said, but it amounts to the same. And no, the way I stated it, my conductor ampacity cannot exceed the 75?C column's ampacity value. Dennis is talking about the conductor.Not exactly what Dennis said. Your conductor ampacity can exceed the 75? C ampacity after derating. Sounds like he's not talking about the conductor.