240.4(B) Overcurrent Devices Rated 800 Amperes or Less.
The next higher standard overcurrent device rating (above
the ampacity of the conductors being protected) shall be
permitted to be used, provided all of the following condi-
tions are met:
(1) The conductors being protected are not part of a branch
circuit supplying more than one receptacle for cord-
and-plug-connected portable loads.
(2) The ampacity of the conductors does not correspond
with the standard ampere rating of a fuse or a circuit
breaker without overload trip adjustments above its rat-
ing (but that shall be permitted to have other trip or
rating adjustments).
(3) The next higher standard rating selected does not ex-
ceed 800 amperes.
With a Zinsco breaker I don't think it makes any difference how it is marked![]()
It seems that the Zinsco Bolt-Ons are able to do their intended job many years after they were installed. Plug-in type if given the only choices of Zinsco or FPE, I'll take FPE.Those choices are like being give the choice of a dog turd or cat turd sandwich though, thank goodness they are obsolete but have seen a few pallets of unused Challenger branded FPE panels on a local online auction, if they had gone for $5 might have got em for the scrap value, but would have liked to see the buyers face when they priced out breakers....:lol: