srinivasan
- Bangalore,India
Field tranmitter has 4-20 ma output which is connected to plc. plc output supply to transmitter is 24Vdc. but in field transmitter side receives only 16.5 Vdc. What will be the causes for voltage drop.
Could also be 250 ohm series resistor in the loop. An older method, but sometimes local indicators with 1-5Vdc input are used in conjunction with the transmitter. The resistor creates a 1-5Vdc drop across it for input to the indicator.
Here's what the manual states...yeah, used model is 3051 cg rosemount pressure transmitter with local indicator. my question is, if 16.5 voltage only occurs across the transmitters. will transmitter work properly. what are the test we have to do for transmitter working condition
Power Supply for 4-20 mA HART
Transmitter operates on 10.5 - 42.4 Vdc. The dc power supply should provide
power with less than two percent ripple.
NOTE
A minimum loop resistance of 250 ohms is required to communicate with a
Field Communicator. If a single power supply is used to power more than one
3051 transmitter, the power supply used, and circuitry common to the
transmitters, should not have more than 20 ohms of impedance at 1200 Hz.
Figure 2-19. Load Limitation
Maximum Loop Resistance = 43.5 * (Power Supply Voltage ? 10.5)
The Field Communicator requires a minimum loop resistance of 250Ω for communication
The total resistance load is the sum of the resistance of the signal leads and
the load resistance of the controller, indicator, and related pieces. Note that
the resistance of intrinsic safety barriers, if used, must be included.
While that may work, that's not the proper way to do it, and should only be used as a last resort remedy to keep things running.put ammeter in series with 4-20ma line and measure it over full range?
just scale the plc input to match?
4-20ma circuits often have scaling adjustments called span & elevation or similar names.
As stated by others, voltage drop is dependent on factors other than just the wire. The manual states, "Use shielded twisted pairs to yield best results. To ensure proper communication, use 24 AWG or larger wire, and do not exceed 5000 feet (1500 meters).if wire sizing is not proper. what will be the effect. for 24 v dc and 4-20 ma, our selected cable size is 1.5 sq.mm and 2 core. is it reason for voltage drop
we have used barriers for all transmitters just to regulate the 4-20 ma properly but what we shall do for regulating voltage?Sri - your PLC (or a DCS) that is powering a field device is not a regulated DC voltage source, it is a DC power source that connects to a field device that acts as a constant current controller based on the value of a process variable.
If I get an opportunity while this question is fresh in my mind I will try to perform the voltage monitoring test I just mentioned and report my results.
Transmitter is located in 400 meter from panel. all the instrument cables are armored type and single pair 1.5 sq.mm only.As stated by others, voltage drop is dependent on factors other than just the wire. The manual states, "Use shielded twisted pairs to yield best results. To ensure proper communication, use 24 AWG or larger wire, and do not exceed 5000 feet (1500 meters).
FWIW, 1.5mm? is ~12ohms/km and approximately 2,960cmil, so slightly larger than our 16AWG (2,580cmil, 1.3mm?). 24AWG is 404cmil, 0.205mm?.
You haven't stated the loop length.
Do you mean intrinsic safety barriers? They also contribute to voltage drop.we have used barriers for all transmitters just to regulate the 4-20 ma properly but what we shall do for regulating voltage?
At 400 meters you have about 9-10 ohms (according to my nogginTransmitter is located in 400 meter from panel. all the instrument cables are armored type and single pair 1.5 sq.mm only.
I posted the 3051 formula for loop resistance earlier.Most of the transmitters I have worked with are designed for a maximum of 750 ohms, total loop resistance. Many of the DCS and PLC inputs have an internal 250 ohm resistor that needs to be included in the loop resistance total. Even if you have two devices with 250 ohm resistors, you would have to have an extremely long loop to cause any problem. #18 has about 6.5 ohms/1000'. (13 ohms for both conductors in the cable). Even at 15,000' of cable, you should not have any problems with two devices in the loop.