- Illinois
- retired electrician
I don't see any danger with paralleling conductors of any size, or even of multiple sizes, as long as the rating of the OCPD does not except the ampacity of the smallest conductor, but that is clearly a code violation unless you meet one of the limited exceptions.
The following words, "to supply control power to indicating instruments, contactors, relays, solenoids, and similar control devices, or for frequencies of
360 Hz and higher," should be removed from Exception #1. As long as the smallest conductor is protected, there is no safety issue.