Kilowatt rating vs Horsepower rating on same piece of equipment
tim89s
Brush Prairie WA
I got a spec sheet on a piece of equipment today. Under the electrical power heading it read 25kw in SI or 33.5 HP in Imperial System. It is 3 phase 240 volt. The piece of equipment is used to make small boxes, it has a few small motors and some heating elements to heat the glue. How do I size the conductors for this piece of equipment? Do I use table 430.250 or do I find the amperage from the 25kw. From the table you have to estimate, so I estimated 90 amps. From the 25kw I got 60.24 amps 250000/240 x 1.73. That a 30 amp difference. I know I am missing something but not sure what. Thanks in advance
First off 33.5 HP is not a standard size motor listed in tables near the end of art 430. But I also am guessing this may not be a single motor machine.
25 kW doesn't mean a lot when sizing conductors if there is a power factor involved either. Throw in some power factor along with teh kW and you will have a calculated necessary ampacity closer to what is in the tables in art 430.
Add: 25 kW is likely motor output power, and input power will also need to add any losses to account for motor efficiency.
Yes there are several little motors. The power factor is .8. Even after doing the calculation I get
76 amps which is still a big difference from the amperage from the table. My issue is the panel I am coming out of will take a max 100 amp breaker. If I use the amps from the hp table I will
need a 125 amp breaker
If the nameplate rating of the equipment is given as 25kW at 0.8pf, I would think that this is total input rating including motors and heaters. The combination of motors and heaters can't really be described in terms of equivalent HP. On this basis, I agree with your 76A calculation. I don't know what code issues you might need to take into account. I'm not from NEC land.