Circuit Breakers Required to be Below 48" for ADA Accessibility???

Status
Not open for further replies.

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Anyone care to figure the fault current for me.
208/120 75KVA 3 phase POCO transformer, 3.6% impedance.
3 parallel runs of 350Kcmil Al, 68' tansformer to tap box on service.

One other thing to add to the mix. What is the upstream distribution? Are there any fuses in the mix? Main disconnect, meter center etc.?
 