davidj792
Member
- Location
- California
The main panel is rated 200amps w/ no main breaker, has bus bar w/qty.6 locations for breakers. Currently contains qty.2- 100amp breakers feeding sub-panels. Qestion 1, If qty.2 seperate 40amp pv breakers are added to this bus bar, this would be considered a supply-side connection and not subject to the 120% rule, correct?? Question 2, per 2011 NEC 705.12 (A), am I correct in interpreting that the qty.2 new pv breakers ( 40amp each ), don't exceed the rating of the service conductors rated 200amps, and the existing 100amp feeders for the subpanels aren't included in that calculation.??