phantom voltage on abandonded conductors

Status
Not open for further replies.
A friend of mine asked me to check out the wiring in an old building she had bought. There was some new and some real old wiring. Long story short some of the old in floor receptacles upstairs are still showing .5 to 4 volts. I figured its coming from wiring in the ceiling of the downstairs but basically don't know if it would be a hazard or not to leave the wires in the floor, but will probably remove them regardless.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
A friend of mine asked me to check out the wiring in an old building she had bought. There was some new and some real old wiring. Long story short some of the old in floor receptacles upstairs are still showing .5 to 4 volts. I figured its coming from wiring in the ceiling of the downstairs but basically don't know if it would be a hazard or not to leave the wires in the floor, but will probably remove them regardless.
Check by using a low impedance meter to see whether these are really phantom voltages or are capable of delivering significant current at those voltages.
4 volts is near the threshold for being sensed by touch with wet skin.
 