Here's a puzzler. We rehabbed a legacy power supply that was feeding yard loads - 120/208V. This was fed from a 277/480V (Delta) supply, and stepped down (120/208V Wye) before being distributed to the branch circuits. When we did the rehab, we put a meter upstream of the stepdown transformer in the 480V and here's what measures at the meter panel:
Meter line in:
A,B,C to Neutral - all 277V
A-B,B-C,C-A - all 480V
Cool so far, but then when we set the meter, load out:
A-Neutral - 480V
B-Neutral - 480V
C-Neutral - 15V (that is not a typo)
Ph-Ph were all 480V
And the meter would not energize
We tried two different meters and got the same results. I know there is something "obvious" here, I'm just missing it. Thanks for any insight.