jtinge
Senior Member
- Location
- Hampton, VA
- Occupation
- Sr. Elec. Engr
Was wondering if the KAIC rating on a breaker is an absolute value or is there some tolerance to the value. The basis for this question being that I ran across a situation where I calculated an available short circuit current of 10.5kA but the existing breaker is rated at 10KAIC. Can the breaker tolerate a some percentage of s.c.c. above the KAIC rating, similar to voltage tolerances on equipment, or does the breaker need to be changed with one having a KAIC rating above 10.5KAIC? If there is a tolerance, what is it and is it defined by UL or the equipment mfrs?