Hello everyone. We are adding a generator to a existing home. The existing service is 600A which is over sized because the original engineer used the optional calculation to size the service but took the pool panel at 100% and didnt bother taking advantage of the 40% reduction at the service level after the first 10 kVA.
We are now adding a generator to the house. Our demand load is 310 Amps. Rather then typing my whole question, I just drew a diagram. Please see attached. My thinking is that the feeder will need to be rated for 600A, not 400A but I would like some input. Thanks in advance.