I have a PV system where the service is 208V 3P, and the available PV inverters are 480V 3P. These are three 12KW SMA inverters. Normally if the inverters were the same voltage as the service, I would combine the 3 inverters using a Main Lug subpanel, then connect the output to the utility line side through a fused disconnect. My question is on the OCPD's using the step down transformer. Do I need to add a separate OCPD between the main lug panel that is combining the inverters and the transformer primary? Then I would use a sub panel that has a main breaker as well as the individual breakers for each inverter. Also, regarding 450.3B, the primary side is the inverter side, but the secondary sees the utility 208V as a primary even though there should be no load. Thanks for any discussion regarding this.