stew
- federal way,washington
Trying to get some ideas as to how others may approach this. Existing 200 outdoor service that needs to be relocated to a new wall in the new garage addition. Currently being fed from a 200 3/r. 1/0 copper from one 100 amp breaker to a panel in the basement located about 20 ft down the current carport and then down to a Bulldog panel. All run in the carport to a J box . all done in rigid 1 1/4 pipe!. Then another /1/4 rigid out of the current service panel down the outer wall about 2 ft and then thru an LB to the furnace and range downstairs again. # 2 cu..
Need to restrike the service at the new outer wall of the new garage enclosure about 20 ft away. Thinking of using an all in one meter main with feed thru lugs to a 150 or 175 disco for the main feeders to the Bulldog panel which I will replace with a 20/40.. Then using a 100 amp breaker in the all in one for the furnace and a 50 for the range. That would require a single 1 1/4 for the refeed to the exisiting J box of the 1/0 cu across the garage in some fashion. Then another 1 1/4 across for the other 100 amp feeder and circuit for the range to a new J box to tie those in to exisiting. Tyring to come up with the least expensive way and this seems like it may be the way to go?
What say ye?
What say ye?