- Tennessee NEC:2017
- Semi-Retired Electrician
I'd be most concerned about chafing on the conductor insulation. That looks like it's before the meter can. Doesn't poco maintain that? And I wonder if it's still moving.
I was also wondering/concerned about any stress this might have put the conductors under inside the meter can.
If it moved once it will move again.
Probably if there were enough slack in the conductors.Would an expansion coupling prevented this?
Expansion coupling to rejoin the pipe. If you want to go all out you could dig down to the ninety put a small hole in it and add some gravel under and around the pipe.
If it were my house I would do what petersonra suggested.
300.5(J) Earth Movement. Where direct-buried conductors, raceways, or cables are subject to movement by settlement or frost, direct-buried conductors, raceways, or cables shall be arranged so as to prevent damage to the enclosed con-ductors or to equipment connected to the raceways.
FPN: This section recognizes ?S? loops in underground direct burial to raceway transitions, expansion fittings in raceway risers to fixed equipment, and, generally, the pro-vision of flexible connections to equipment subject to settlement or frost heaves.
The picture is why this code section exists.
This doesn't seem to be the case in this instance, but I've heard that problems similar to this can be caused by setting the conduit riser in the concrete slab rather than sleeving it. Can somebody elaborate on that for me? I'm having a hard time picturing it in my head. Thanks.
They are stiil pumping water inside the pipes inside the Hoover dam to keep the curing concrete cool.
A prescription of Xanax should take care of that:lol: