SEU Protection

Learn the NEC with Mike Holt now!

SEU Protection

  • Yes

    Votes: 5 31.3%
  • No

    Votes: 11 68.8%

  • Total voters
    16
  • Poll closed .
Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
In some areas they use combination type inspectors that may not even be electricians. Do you really want to trust their opinion or use your own knowledge and play it safe?


I think most electricians will look at this install and say yes it is subject to physical damage and needs to be protected.

If the electrician is to dumb to think the cable should be protected then the inspector should have caught it.

IMO it's subject to physical damage but in this case the two opinions that matter are those of the installer and the inspector. They both see it differently or the inspector never really looked at it closely. :roll:
 

jusme123

Senior Member
Location
NY
Occupation
JW
In my honest opinion, if the SEU was to be damaged by some means of physical damage, than even if another wiring method was installed, that would have failed as well....

I disagree, what if I ran 2" rigid into building out of the bottom of the meter. It would have to take a lot of abuse
 