+1If you lose the service grounded conductor, you will energize the pool bonding grid, if there is a connection to the EGC. In most cases there will be at the pool pump. There will be a serious hazard between the anything that is connected to the pool grounding grid and the earth. This same hazard will also exist between anything connected to the electrical grounding system and earth.
Short of some sort of open neutral protection that will open the ungrounded conductors if the neutral is lost, I don't know of anything that could provide protection from this problem.
See my post above. (Ships that pass in the night....)Don't think that it would trip the G.F.C.I..
Curious about Don's comment about the hazard at the pool with an open grounded conductor at the service. I thought that was the reason for bonding everything that pertained to the pool including the pump motor to keep everything at the same touch potential.
I can't say that it wouldn't be hazardous. I am just curious if the equipotential bonding grid would make a difference? I am not talking about the g.f.c.i. but the shock hazard if everything is properly bonded.
But depending on the amount of connected unbalanced load at the time and the ground electrode system resistance, a hazardous offset of the EGC from ground will not be easily distinguishable from a supply voltage dip.GFCI should be made to open when you loose a neutral, something like a 120 volt holding relay.
That would assume that the equipotential grid was correctly installed, and there is still a lot of debate as the the effectiveness of the single bonding wire that the code permits to be used for the perimeter surface.+1
Since by losing the service neutral you have lost both the copper bond of the EGC and the neutral grounded conductor, the only return current path will be through the ground electrode system. That will not trip a protective breaker anywhere and will probably (although not guaranteed) not generate enough of a line-neutral current imbalance to trip any GFCI.
Although the entire pool grid would be raised above earth ground, it would still serve as an equipotential grid and would prevent any touch or step hazards in and around the pool all the way up to the point that you step off the pool deck. At that point one can only hope that you are stepping quickly and fall in the right direction.![]()
A very good point, especially for a situation like the one described where a high current is flowing through the EGC and the earth surrounding the electrodes.That would assume that the equipotential grid was correctly installed, and there is still a lot of debate as the the effectiveness of the single bonding wire that the code permits to be used for the perimeter surface.
Can you make the water in a pool the same potential as the pool deck and other parts of the grounding grid ?
If you loose the neutral at the weather head, what good would a GFCI do to protect a pool.
It will not trip the GFCI, there is no current imbalance on the load side. Voltage imbalance - very likely but it does not monitor for that. A pool with a well installed equipotential bonding system installed should shunt any current away from users. Current is still there, but finds paths of lower resistance than the user to follow. If some item is missed when making up the bonding system that is where dangerous potentials may show up or if some part of the bonding system is damaged.Don't think that it would trip the G.F.C.I..
Curious about Don's comment about the hazard at the pool with an open grounded conductor at the service. I thought that was the reason for bonding everything that pertained to the pool including the pump motor to keep everything at the same touch potential.
I can't say that it wouldn't be hazardous. I am just curious if the equipotential bonding grid would make a difference? I am not talking about the g.f.c.i. but the shock hazard if everything is properly bonded.
After looking at GoldDiggers reply. I kind of agree with him.
There are such devices. Usually found on portable cordsets with integral GFCI. There must be full voltage before they will reset, and if any supply conductor is interrupted they drop out.GFCI should be made to open when you loose a neutral, something like a 120 volt holding relay.