I'm new to the MH Forums, I have a plan checker in So Cal that issued a PV plan correction for the following: Provide Calculations for the Load Center and the conductors between the Load Center and the Main Service Panel per 690.64(B)(2).
My main panel is 225a and main breaker is 200a. I am backfeeding the PV with a 45a breaker. For the Sub Panel (load center) I have a 100a loadcenter, with 1 - 20a 2p breaker and 1 - 25a 2 pole breaker. He has indicated that based on 690.64(B)(2) I have to calculate for the sub panel as well as the conductors between the sub panel and the main service panel
So my calcs are Sub Panel: 100a 20+25+45x1.2=108a.
Conductors: 20+25+45/1.2=75a.
So the 100a panel is adequate based on calc. The conductors will need to be #4 (82.65 allowable ampacity) from my chart based on 113f. I guess my question is, is, I have never calc'd for the conductors in this manner (having to add the breakers from the service panel and subpanel then dividing by the 1.20 rule. Is my sub panel and conductor calcs correct?
My main panel is 225a and main breaker is 200a. I am backfeeding the PV with a 45a breaker. For the Sub Panel (load center) I have a 100a loadcenter, with 1 - 20a 2p breaker and 1 - 25a 2 pole breaker. He has indicated that based on 690.64(B)(2) I have to calculate for the sub panel as well as the conductors between the sub panel and the main service panel
So my calcs are Sub Panel: 100a 20+25+45x1.2=108a.
Conductors: 20+25+45/1.2=75a.
So the 100a panel is adequate based on calc. The conductors will need to be #4 (82.65 allowable ampacity) from my chart based on 113f. I guess my question is, is, I have never calc'd for the conductors in this manner (having to add the breakers from the service panel and subpanel then dividing by the 1.20 rule. Is my sub panel and conductor calcs correct?