If your second wall outlet is outside that area, or if it is something special not covered by 210.52(A), then it can't be on the same circuit as your refrigerator.210.52(B)(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
The way I read its wording, the section you quoted does not say that. It says that there must not be any of the three specific types of required and refrigeration outlets in those rooms that are not on one of the SABCs.As long as both receptacles are in the "kitchen, pantry, breakfast room, dining room, or similar area," then you are fine. Your 20 amp circuit will be considered an additional SABC per 210.52(B)(1):
If the quote said "shall serve only....", then it would mean what you say.
(There is no prohibition on putting additional outlets in those areas which are not on an SABC as long as they really are in addition to the required outlets.)
Now your point of view may be supported by a different quote from the Code.
Customer wants the refrigerator in the pantry.I will run a dedicated 20a 120v line to the refer. I would like to also feed a wall outlet of this outlet. No counters or sinks involved. Two other circuits already feed the counters in the kitchen.
Opinions? Thanks.
The ref does not need a dedicated circuit nor does it need and outlet behind it. It is legal to plug it into the counter top outlet. Not good practice but legal. You can also install a dedicated 15 amp circuit for the ref. only. Has any body seen a clock above the ref since the 1950's?
It used to be common practice to plug the fridge into an adjacent countertop receptacle due to the fact that the fridges had to be unplugged to be defrosted back then.
210.52 (B) (1) Exception No. 2: says a receptacle outlet for refrigeration shall be permitted to be supplied from an individual branch circuit. By definition, an individual branch circuit is one that supplies only one utilization equipment. So I would say nothing else would be allowed to use it.![]()
I would say that "be permitted" is a lot more key that "shall" in this case.exception and shall are the key words here.
Also, there was no outlet behind where you put the refrigerator because the icebox it replaced did not need one. (Really old!)
(And maybe you ran a cord to the pendant light which was the closest outlet in the kitchen.)
You could also adjust the thermostat - they usually had an "off" position. I think you still can find newer refrigerators without automatic defrost, especially in the lower line models commonly used in apartments.It used to be common practice to plug the fridge into an adjacent countertop receptacle due to the fact that the fridges had to be unplugged to be defrosted back then.