junkenpo621
New member
- Location
- Oakland, CA
Hi All,
I'm trying to get confirmation on a code interpretation here. Let me give some background. My team and I have been "debating" for weeks regarding landing the combined AC GEC/EGC as permitted in 690.47(C)(3) in a subpanel bus bar, then running a new conductor back to the MSP to either land in the grounding bar or to be irreversibly crimped to the existing GEC. The interpretation comes in from 250.64(C) where sections of bus bars are allowed to be used to form a continuous GEC. It also states that the GEC is permitted to land in the "Associated AC Equipment." Half of the team thinks it is permissible to run this GEC to the subpanel grounding bar (or AC disconnect or PV meter) then run a new conductor from the enclosure to the existing GEC. The other half believes that the GEC must be unbroken and not terminated all the way to either landing in the MSP grounding bar or to where it is irreversibly crimped to the GEC and the only way you can use a second conductor is with a crimp.
We've been struggling over this for a while now and have had the input of some notable people in the PV industry, but their interpretations are (of course) divided on the matter. I was hoping that some healthy, open dialogue would help in the matter and I thank you all in advance for your input!
I'm trying to get confirmation on a code interpretation here. Let me give some background. My team and I have been "debating" for weeks regarding landing the combined AC GEC/EGC as permitted in 690.47(C)(3) in a subpanel bus bar, then running a new conductor back to the MSP to either land in the grounding bar or to be irreversibly crimped to the existing GEC. The interpretation comes in from 250.64(C) where sections of bus bars are allowed to be used to form a continuous GEC. It also states that the GEC is permitted to land in the "Associated AC Equipment." Half of the team thinks it is permissible to run this GEC to the subpanel grounding bar (or AC disconnect or PV meter) then run a new conductor from the enclosure to the existing GEC. The other half believes that the GEC must be unbroken and not terminated all the way to either landing in the MSP grounding bar or to where it is irreversibly crimped to the GEC and the only way you can use a second conductor is with a crimp.
We've been struggling over this for a while now and have had the input of some notable people in the PV industry, but their interpretations are (of course) divided on the matter. I was hoping that some healthy, open dialogue would help in the matter and I thank you all in advance for your input!