Im wiring a warehouse,the J beams on the ceiling are are covered with insulation down to the bottom of the J beam. the insulation has
metal strapping holding up the insulation.most metal buildings Ive worked in the insulation was on top of the j beam.Is it ok to clip the
MC to the bottom of the j beam. I would consider this exposed wiring.
 

wireday

Senior Member
Location
New England
Occupation
Master electrician
Thanks Dave, my concern was having the mc down on the bottom of the J beam,I know running with the beam would be ok.The J beams
are 5 feet apart so if I go from one to another its still under 6 feet for supporting.
 