Identifying Isolated grounding conductor
Bearj1506
New member
I recently pulled both equipment and isolated grounding conductors in a conduit and someone said the Isolated grounding conductors must be green with a yellow stripe .(I marked with phase tape)IS this so? reference in code as I may challenge if required by inspector.
There's nothing in the NEC that would require the yellow stripe for an IG. You could use green with a yellow stripe for the standard EGC and a green conductor for the IG.
+1
As long as the two wires are distinguishable and the various marking alternatives are each used uniformly through the facility.
+1
I'm wondering if it's actually required that you distinguish between the two?
Well, the isolated ground is supposed to run back to the panel, without interconnecting to other non-isolated grounds along the way, I believe.
So if the wiring goes through other device boxes, it is important to distinguish.
It may not be a code requirement but it is a practical one.
(There is also a possible difference between an isolated ground connection and a redundant ground ground connection (which is, I believe, standard in Hospital Grade.))