Bending Radius of DLO vs Box size.
Bending Radius of DLO vs Box size.
Hi...we are using Diesel Locomotive cable for a project. We need to terminate these cables in a junction box. I am looking at the NEC for direction on sizing this box based on conduit sizes entering the box (Art. 314.28) and the bending radius distance specified in Table 312.6(B). Because this cable is so flexible and has a small minimum bending radius, can I take that into account when sizing this box? I understand the minimum box size based on conduit sizes, but it seems that I can use a smaller bending radius distance with this High Flex cable.
I recently installed an emergency generator at my home and intercepted the 200 Amp utility feed (THHN) in plastic conduit with two 4"x 4" x 3" pull boxes (to insert the ATS). Then used # 1/0 DLO cable (3-1/c) which installed with no problem.
The town inspector never heard of "DLO" went back to his office and called me: Rejected ! (Since it was my basement, I overruled him).
The code allows a lot of qualified exceptions (which can be allowed if the inspector has an engineering degree and is also experienced). A small town inspector is (usually) an electrician who has read the NEC code twice and will not deviate from it (for lack of education on the subject).
How large a box is needed ? You must be able to install the cable(s) without damaging or over bending it. The termination studs need clearances per code. Its that simple.
We design large drive control systems for conveyors and bulk material handling machines often using custom-made pull boxes, never had an inspection problem.