Right there is your answer, and your misunderstanding of the requirement. The rebar is NOT PRESENT and/or accessible. Therefore not required to be used.250.50 states "All grounding electrodes as described in 250.52(A) (1) through (A) (7) that are present at each bldg or structure served shall be bonded together to form the grounding electrode system.
Now if he was pouring the pad, then the rebar is Present and shall be used.